Robust adaptive stabilization by delay under state parametric uncertainty and measurement bias - Inria - Institut national de recherche en sciences et technologies du numérique Accéder directement au contenu
Article Dans Une Revue IEEE Transactions on Automatic Control Année : 2021
An output robust adaptive control is designed for a class of Lipschitz nonlinear systems under assumption that the measurements are available with a constant bias and the state equations linearly parameterized by unknown parameters and external disturbances. A dynamic state reconstruction (synthesis of an observer) is avoided by using delayed values of the output in the feedback and adaptation laws. The analysis of robust stability for the resulted time-delay system is performed by using the Lyapunov-Krasovskii approach. The control and adaptation gains can be selected as a solution of the proposed linear matrix inequalities. This research is motivated by a nonlinear pendulum control problem, and the efficacy of the developed control is demonstrated on this application through experiments.
Adaptive_TD_J.pdf (543.45 Ko) Télécharger le fichier
hal-03059893 , version 1 (13-12-2020)
Jian Wang, Stanislav Aranovskiy, Emilia Fridman, Dmitry Sokolov, Denis Efimov, et al.. Robust adaptive stabilization by delay under state parametric uncertainty and measurement bias. IEEE Transactions on Automatic Control, 2021, 66 (11), pp.5459-5466. ⟨10.1109/TAC.2020.3045125⟩. ⟨hal-03059893⟩
497 Consultations
487 Téléchargements