Fault diagnosis of industrial systems by conditional Gaussian network including a distance rejection criterion - Inria - Institut national de recherche en sciences et technologies du numérique Accéder directement au contenu
Article Dans Une Revue Engineering Applications of Artificial Intelligence Année : 2010
The purpose of this article is to present a method for industrial process diagnosis with Bayesian network, and more particularly with conditional Gaussian network (CGN). The interest of the proposed method is to combine a discriminant analysis and a distance rejection in a CGN in order to detect new types of fault. The performances of this method are evaluated on the data of a benchmark example: the Tennessee Eastman Process. Three kinds of fault are taken into account on this complex process. The challenging objective is to obtain the minimal recognition error rate for these three faults and to obtain sufficient results in rejection of new types of fault.
verron10a.pdf (582.9 Ko) Télécharger le fichier
inria-00516954 , version 1 (13-09-2010)
Sylvain Verron, Teodor Tiplica, Abdessamad Kobi. Fault diagnosis of industrial systems by conditional Gaussian network including a distance rejection criterion. Engineering Applications of Artificial Intelligence, 2010, 23 (7), pp.1229-1235. ⟨10.1016/j.engappai.2010.05.002⟩. ⟨inria-00516954⟩
Collections
UNIV-ANGERS
86 Consultations
373 Téléchargements